Engineering Board Exam Reviewer · Three-Phase Systems in Power Applications · hard

A three-phase, four-wire wye system with a 120 V phase voltage (VAN=120 0°, VBN=120 -120°, VCN=120 120°) feeds the unbalanced resistive loads shown: RA=8, , RB=10, , and RC=24, . Find the neutral current in polar form.

  1. 8.89 43° A
  2. 32 0° A
  3. 8.89 137° A
  4. 8.89 -43° A

Answer

D. 8.89 -43° A

Solution

The line currents are IA=120 0°/8, =15 0° A, IB=120 -120°/10, =12 -120° A, and IC=120 120°/24, =5 120° A. The neutral wire carries their phasor sum: IN=IA+IB+IC=8.89 -43° A.

More Three-Phase Systems in Power Applications questions

  1. The balanced load shown has Z=30+j40, in each phase and is wye-connected to a 400 V line. If the same three impedances are reconnected in…
  2. A three-phase generator is rated 1500 kVA at 4160 V (line-to-line). What is its rated line current?
  3. Three 10, resistors are connected in delta across a 240 V three-phase line. What is the line current?
  4. A balanced three-phase load of 100 kW operates at 0.8 power factor lagging. How many kvar of capacitors are needed to raise the power…
  5. In the two-wattmeter method on a balanced three-phase load, the wattmeters read 5 kW and 3 kW. What is the load power factor?
  6. The 30 kW, 0.8 power factor lagging three-phase load above is supplied from a 480 V line. Find its total reactive power.
  7. A balanced three-phase load takes 30 kW at 0.8 power factor lagging from a 480 V line. Find the line current.
  8. A balanced delta-connected load, with Z=6+j8, in each phase, is supplied from a three-phase line of 400 V (line-to-line, rms). Find the…
  9. A balanced delta-connected load, with Z=24+j18, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  10. A balanced delta-connected load, with Z=12+j9, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…

All Three-Phase Systems in Power Applications questions