Engineering Board Exam Reviewer · Three-Phase Systems in Power Applications · medium

A balanced delta-connected load, with Z=12+j9, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the current in each load impedance (the phase current).

  1. 24 A
  2. 8.01 A
  3. 27.7 A
  4. 13.9 A

Answer

D. 13.9 A

Solution

In a delta connection each phase impedance sees the full line voltage: Iph=VL/|Z|= 208 V15, =13.9 A.

More Three-Phase Systems in Power Applications questions

  1. A balanced wye-connected load, with Z=15+j20, in each phase, is supplied from a three-phase line of 480 V (line-to-line, rms). Find the…
  2. A balanced wye-connected load, with Z=16+j12, in each phase, is supplied from a three-phase line of 400 V (line-to-line, rms). Find the…
  3. A balanced wye-connected load, with Z=15+j20, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  4. In a balanced three-phase, four-wire wye system the current in the neutral conductor is
  5. A balanced three-phase load draws 10 A from a 400 V line at a power factor of 0.8. What total real power does it absorb?
  6. A wye-connected three-phase source has a line-to-line voltage of 480 V. What is its phase voltage?
  7. The three voltages of a balanced three-phase supply are displaced from each other by
  8. In a balanced delta-connected load, the relationship between the line current IL and the phase current Iph is
  9. In a balanced wye-connected system, the relationship between the line voltage VL and the phase voltage Vph is
  10. The balanced wye-connected load shown is supplied from a three-phase line of 240 V (line-to-line, rms). What is the voltage across each…

All Three-Phase Systems in Power Applications questions