Engineering Board Exam Reviewer · Three-Phase Systems in Power Applications · easy
A balanced three-phase load draws 10 A from a 400 V line at a power factor of 0.8. What total real power does it absorb?
- 3.2 kW
- 5.54 kW
- 9.6 kW
- 6.93 kW
Answer
B. 5.54 kW
Solution
P= 3,VLIL = 3(400)(10)(0.8)=5543 W=5.54 kW.