Engineering Board Exam Reviewer · Three-Phase Systems in Power Applications · medium

In the two-wattmeter method on a balanced three-phase load, the wattmeters read 5 kW and 3 kW. What is the load power factor?

  1. 0.25
  2. 0.918
  3. 0.6
  4. 0.397

Answer

B. 0.918

Solution

= 3,W1-W2/W1+W2= 3,2/8=0.433 =23.4°. PF= 23.4°=0.918 (total power =8 kW).

More Three-Phase Systems in Power Applications questions

  1. The 30 kW, 0.8 power factor lagging three-phase load above is supplied from a 480 V line. Find its total reactive power.
  2. A balanced three-phase load takes 30 kW at 0.8 power factor lagging from a 480 V line. Find the line current.
  3. A balanced delta-connected load, with Z=6+j8, in each phase, is supplied from a three-phase line of 400 V (line-to-line, rms). Find the…
  4. A balanced delta-connected load, with Z=24+j18, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  5. A balanced delta-connected load, with Z=12+j9, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  6. A balanced wye-connected load, with Z=15+j20, in each phase, is supplied from a three-phase line of 480 V (line-to-line, rms). Find the…
  7. A balanced wye-connected load, with Z=16+j12, in each phase, is supplied from a three-phase line of 400 V (line-to-line, rms). Find the…
  8. A balanced wye-connected load, with Z=15+j20, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  9. In a balanced three-phase, four-wire wye system the current in the neutral conductor is
  10. A balanced three-phase load draws 10 A from a 400 V line at a power factor of 0.8. What total real power does it absorb?

All Three-Phase Systems in Power Applications questions