Engineering Board Exam Reviewer · Three-Phase Systems in Power Applications · medium

The 30 kW, 0.8 power factor lagging three-phase load above is supplied from a 480 V line. Find its total reactive power.

  1. 22.5 kvar
  2. 18 kvar
  3. 37.5 kvar
  4. 45 kvar

Answer

A. 22.5 kvar

Solution

S= P PF=30/0.8=37.5 kVA. Q=S =37.5(0.6)=22.5 kvar.

More Three-Phase Systems in Power Applications questions

  1. A balanced three-phase load takes 30 kW at 0.8 power factor lagging from a 480 V line. Find the line current.
  2. A balanced delta-connected load, with Z=6+j8, in each phase, is supplied from a three-phase line of 400 V (line-to-line, rms). Find the…
  3. A balanced delta-connected load, with Z=24+j18, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  4. A balanced delta-connected load, with Z=12+j9, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  5. A balanced wye-connected load, with Z=15+j20, in each phase, is supplied from a three-phase line of 480 V (line-to-line, rms). Find the…
  6. A balanced wye-connected load, with Z=16+j12, in each phase, is supplied from a three-phase line of 400 V (line-to-line, rms). Find the…
  7. A balanced wye-connected load, with Z=15+j20, in each phase, is supplied from a three-phase line of 208 V (line-to-line, rms). Find the…
  8. In a balanced three-phase, four-wire wye system the current in the neutral conductor is
  9. A balanced three-phase load draws 10 A from a 400 V line at a power factor of 0.8. What total real power does it absorb?
  10. A wye-connected three-phase source has a line-to-line voltage of 480 V. What is its phase voltage?

All Three-Phase Systems in Power Applications questions